Our full technical support staff does not monitor this forum. If you need assistance from a member of our staff, please submit your question from the Ask a Question page.


Log in or register to post/reply in the forum.

How to connect to Pulse flow meter to CR1000


MikelisD Dec 11, 2017 01:43 PM

Hello, 

Can someone suggest how to connect the Digimesa FM935-1500

https://www.tme.eu/en/Document/e44ffff8809c5a2143a01abd4a419033/935-1500X.PDF

to CR1000. 

And do I need the resistor and capacitator showed in the data sheet? 


JDavis Dec 11, 2017 08:30 PM

If you use a P channel in switch closure mode, it will probably work directly on the CR1000. There is a chance that the datalogger won't pull the voltage high enough.

If the first option isn't working, use a 100 kOhm resistor from 12V to a P or C channel. It should read just fine them. Switch closure mode uses a capacitor for debounce. High frequency mode does not debounce.


MikelisD Dec 12, 2017 02:55 PM

Thanks, it worked actually directly in P, had the wrong type of signal selected previously.

However it is flactuating in sample value, for example 4 and 5 pulses/s. If doing averages of 4 s, still every other average flactuates. The average value between samples or 2 averages seems to be correct, but I would like to know how to correctly choose sampling time or output time to have stable value.


JDavis Dec 12, 2017 04:49 PM

If you do averages on a longer time interval, you will see more resolution.

For example if the sensor outputs 4.5 pulses per second and you use a 1 second scan, one scan will have 4 pulses and the next 5 pulses. Scan to scan, the flow number will bounce back and forth. The resolution on a 1 second scan is 1 pulse per second.

If you did a 10 second scan(or saved an average to a 10 second table), you would get 45 pulses. The average is 45 pulses/10 seconds. The average will correctly show 4.5 pulses per second. You wouldn't see the reading bounce on the longer time interval.

The resolution on a 10 second interval is 1 pulse/10 seconds, which is 0.1 pulses per second. The resolution on your average goes up with longer intervals.

 


Gregory12 Mar 14, 2025 11:07 AM

You can connect the Digimesa FM935-1500 to the CR1000 via pulse output using the CR1000's digital input. According to the datasheet, you may need a pull-up resistor (10 kΩ) and capacitor (100 nF) to stabilize the pulse signal, but double check the CR1000's requirements to make sure the input signal is suitable. 